DirtyBear

Junior Member

Daul 400 MPS flow Sensors

Sunday, February 5th 2017, 11:20pm

Hi
Is it possible to have 2 400 MPS flow and 2 Aqualls connect to one 6XT ? ?(
Anyone can help ?

This post has been edited 1 times, last edit by "DirtyBear" (Feb 6th 2017, 12:05am)

InfoSeeker

Senior Member

Tuesday, February 7th 2017, 2:58am

Yes.

The aquabus can address up to four MPS devices (12. 13. 14, 15).
The two MPS 400 flow sensors will each take one address.
Assuming you are referring to the aqualis with built in level sensor, then two of those would take up the balance of the available addresses.

MPS addresses can be assigned in aquasuite under the system tab for each device.

DirtyBear

Junior Member

Wednesday, February 8th 2017, 6:16pm

That means I can only 2 400 flow sensors and 2 aqualis and I can not connect the D5 usb pumps

This post has been edited 1 times, last edit by "DirtyBear" (Feb 8th 2017, 6:17pm)

InfoSeeker

Senior Member

Thursday, February 9th 2017, 5:44am

The aquabus has four (4) MPS device addresses available.

If both aqualis reservoirs have the built-in level sensors, then the additional two MPS 400 flow sensors would max out the aquabus' MPS addresses.

You will still be able to manually control the two D5 USB/aquabus pumps with the USB connection.
Pumps are generally considered set & forget anyway, so that would be a viable option.

If you want the D5 USB/aquabus pumps to be integrated with the aquaero, then either the flow sensors or the level sensors would have to go USB connection only.

It appears you have six MPS devices, so you will have to select which four you want to integrate with the aquaero.

DirtyBear

Junior Member

Thursday, February 9th 2017, 11:26am

Many Thx :thumbsup: