Dear visitor, welcome to Aqua Computer Forum. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

Pressure cycling

Sunday, October 23rd 2022, 10:32am

When my leak shield starts up in to monitor mode it really overshoots the pressure and end up in a strange cycling patter until it finally settles to the correct pressure.


Any suggestions

red-ray

Junior Member

Post a screen shot of the whole X.59 Status screen

Sunday, October 23rd 2022, 11:18am

Mine has never done this and from just the graph I can't even guess what may be causing this. Post a screen shot of the whole X.59 Status screen and also export the event log and attach it

This post has been edited 1 times, last edit by "red-ray" (Oct 23rd 2022, 11:20am)

Sunday, October 23rd 2022, 12:41pm



There's nothing exciting in the logs just the cycling effect.

red-ray

Junior Member

Sunday, October 23rd 2022, 1:09pm

I am surprised there are no P1 + P2 + Q + D Waterproof Membrane values, but as you failed to post the event log I asked for I can't see what happened before the cycling.

Currently my best guess is that either that the Level Measurement failed or never happened and there is now a lot less than 107ml of air in the reservoir

Were it my system I would do as follows:

1) Save the current event log and then clear it.
2) Set the mode to Release
4) Wait 15 seconds
5) Set the mode to Monitor and see what happens, it should so a Measure Level and then the P1 + P2 + Q + D Waterproof Membrane values should be reported.
6) As to what I would do next would depend on what happened

This post has been edited 1 times, last edit by "red-ray" (Oct 23rd 2022, 1:15pm)

Sunday, October 23rd 2022, 10:04pm

Same as before, there was a warning that the membrane was not function to expectations.


LEAKSHILED 10438-20652
Date: 23 Oct 2022, 22:00
ID: 171 T: 10 23 2022 22:00 Event: ShieldPressureHigh Mode: Monitor State: Protected P: 276.4 P_rate: NaN V_rate: NaN V1: 1000 V2: NaN
ID: 170 T: 10 23 2022 22:00 Event: ShieldPumpFinish Mode: Monitor State: Pump P: 248.2 P_rate: NaN V_rate: NaN V1: NaN V2: NaN
ID: 169 T: 10 23 2022 22:00 Event: ShieldPressureLow Mode: Monitor State: Unprotected P: 52.9 P_rate: NaN V_rate: NaN V1: 500 V2: NaN
ID: 168 T: 10 23 2022 22:00 Event: ShieldPressureHigh Mode: Monitor State: Protected P: 274.2 P_rate: NaN V_rate: NaN V1: 1000 V2: NaN
ID: 167 T: 10 23 2022 22:00 Event: ShieldPumpFinish Mode: Monitor State: Pump P: 225.5 P_rate: NaN V_rate: NaN V1: NaN V2: NaN
ID: 166 T: 10 23 2022 22:00 Event: ShieldPressureLow Mode: Monitor State: Unprotected P: 52.9 P_rate: NaN V_rate: NaN V1: 500 V2: NaN
ID: 165 T: 10 23 2022 22:00 Event: ShieldPressureHigh Mode: Monitor State: Unprotected P: 252.4 P_rate: NaN V_rate: NaN V1: 1000 V2: NaN
ID: 164 T: 10 23 2022 22:00 Event: ShieldPumpFinish Mode: Monitor State: Pump P: 187 P_rate: NaN V_rate: NaN V1: NaN V2: NaN
ID: 163 T: 10 23 2022 22:00 Event: ShieldPressureLow Mode: Monitor State: Unprotected P: 52.8 P_rate: NaN V_rate: NaN V1: 500 V2: NaN
ID: 162 T: 10 23 2022 22:00 Event: ShieldPressureHigh Mode: Monitor State: Protected P: 276.9 P_rate: NaN V_rate: NaN V1: 1000 V2: NaN
ID: 161 T: 10 23 2022 22:00 Event: ShieldPumpFinish Mode: Monitor State: Pump P: 294.2 P_rate: NaN V_rate: NaN V1: NaN V2: NaN
ID: 160 T: 10 23 2022 22:00 Event: ShieldPressureLow Mode: Monitor State: Unprotected P: 52.5 P_rate: NaN V_rate: NaN V1: 500 V2: NaN

red-ray

Junior Member

Sunday, October 23rd 2022, 10:15pm

there was a warning that the membrane was not function to expectations.


Ah, I suspect this is the root cause of the overshoots, but I have no idea what caused this to how to fix it.

It would be sensible to post a screen shot of exactly what was reported, were there any error codes?

I suspect you should email support@aqua-computer.de, include as much detail as possible

This post has been edited 1 times, last edit by "red-ray" (Oct 23rd 2022, 11:27pm)

Monday, October 24th 2022, 6:39am

Probleme mit Leakshield und Fillport


Translation from the above post:

Quoted

Your membrane is clogged. You can see this from the spikes in the pressure curve. Change your coolant and drip a few drops of isopropnaol onto the membrane. Wait 5 minutes, vacuum with kitchen roll without touching and repeat this 5 times. If the peaks remain, then the membrane must be replaced.