Hi
sidefield,
I connected the adapter today and tested several scenarios.
In the Outputs menu I've set the "Controlled from event system" option for the relay. I used pins 2 and 3 (Normally Connected) of the relay and I have set "Relay: On" in Alarm actions.
So, when an alarm condition occurs, the Aquaero opens the relay and the computer powers off. Once the PC is off you can restart it either by going to the settings and changing the relay output to off (it will restart immediately), or by turning off the power to the computer completely and recycling the Aquaero power.
Another way to do it is not to use the ATX break adapter, but to wire the relay contacts 1 & 3 (Normally Open) in parallel to the case Power on switch. Then in Alarm actions set the "Relay: Switch for 10s" action. This would emulate a person holding the case power button and shutting down the computer that way.
If you don't want to loose any unsaved data you can use the later method with the action "Relay: Switch for 2s", thus initiating a standard Windows shutdown procedure. This would be safer for the data, but Windows shutdown procedure can get stuck due to many different reasons...
Now, if only they could fix the tubemeter showing 0% level for a second or two every once in a while and causing false alarms I could have a well protected system.
Kind regards,
Boris.