Problems using Aquastream XT Ultra and Flowmeter

Montag, 17. Dezember 2007, 23:22

If i connect the flowsensor through the Aquastream XT Ultra i get no value, it says 0,0 l/h..

And the under the " Pump and flow rate settings " the Flowsensor Active button is "pressed"

Calibration Value is 509 Impulses pr liter.
Number of measuring pulses is 8.

Anything wrong here?
If i connect i to the Aquaero it works fine.. The Calibration value there is also 509.. Is this right?

Re: Problems using Aquastream XT Ultra and Flowmet

Dienstag, 18. Dezember 2007, 09:25

After setting the pump input to flowmeter you have to restart the pump (power off/on).

Ascubal

Junior Member

Re: Problems using Aquastream XT Ultra and Flowmet

Dienstag, 18. Dezember 2007, 15:10

Thanks, that helped :) But what about the impulses? is that right? I have the "old" flowmeter..

Re: Problems using Aquastream XT Ultra and Flowmet

Dienstag, 18. Dezember 2007, 19:06

Yep Impulse is right.