• 06.10.2026, 15:36
cptninc
Thursday, July 28th 2022, 8:07pm
This is what it's been doing this afternoon. Why would the setpoint be changing so often even though the pressure does not change and the pump doesn't run? Is this because my D5 is changing speeds?
Friday, July 29th 2022, 7:52am
The problem may be that your minimum vacuum is not sufficient to compensate for the pressure of your pump.
According to your picture, the pump is at 360 mbar and your minimum vacuum is 350 mbar, in which case water would leak out if there is a leak and consequently your system is unprotected.
Since the pump speed has only marginal influence on the cooling, you can simply set the pump to a fixed value at which you have enough flow and the pump sounds most comfortable to you.
If you then set the minimum value of the LEAKSHIELD accordingly above the pump pressure, the problem is solved.
Translated with www.DeepL.com/Translator (free version)
cptninc
Monday, August 1st 2022, 3:06am
It seems like simply finishing a render and then loading up a game is enough to trigger the leak warning. How do I manage this?
This is the log from when the warning popped up. The machine was running under steady-state load until 20:46, at which point the coolant temp dropped quite quickly. I have already configured the pump to run at a constant rpm, so that did not change when the coolant temp & system load changed. I also don't understand why there is a big string of "Pressure setpoint changed" entries.
I have also included two screen caps from the different info pages in Aquasuite. Note that the high pump usage on 20:Jul and 21:Jul was when I was trying to adjust settings and is not representative of an actual leak.
Any help with this would be great. At this point, I cannot use the LEAKSHIELD to shield my machine from leaks. I have been forced to disable all alarms.
Source code
1
2
3
4
5
6
7
8
9
10
11
12
13
14
15
16
17
18
19
20
21
22
23
24
25
26
27
28
29
30
31
32
31/07/2022 20:52:33    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 366 mbar
31/07/2022 20:52:32    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 366 mbar
31/07/2022 20:52:09    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 365 mbar
31/07/2022 20:52:01    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 365 mbar
31/07/2022 20:51:50    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 365 mbar
31/07/2022 20:51:39    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 365 mbar
31/07/2022 20:51:28    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 365 mbar
31/07/2022 20:51:26    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 365 mbar
31/07/2022 20:50:59    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 366 mbar
31/07/2022 20:50:54    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 366 mbar
31/07/2022 20:50:36    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 366 mbar
31/07/2022 20:50:34    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 366 mbar
31/07/2022 20:50:23    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 366 mbar
31/07/2022 20:50:18    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 366 mbar
31/07/2022 20:50:08    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 366 mbar
31/07/2022 20:49:52    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 366 mbar
31/07/2022 20:49:41    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 365 mbar
31/07/2022 20:48:49    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 366 mbar
31/07/2022 20:48:38    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 367 mbar
31/07/2022 20:48:28    Event: Pumping finished.                     Mode: SHIELD             State: Establish negative pressurePressure: 422 mbar
31/07/2022 20:48:28    Event: Pressure too low.                     Mode: SHIELD             State: Unprotected       Pressure: 363 mbar
31/07/2022 20:47:54    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 365 mbar
31/07/2022 20:47:43    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 366 mbar
31/07/2022 20:47:39    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 366 mbar
31/07/2022 20:47:28    Event: Pumping finished.                     Mode: SHIELD             State: Establish negative pressurePressure: 422 mbar
31/07/2022 20:47:28    Event: Warning: Pump runs too frequently.    Mode: SHIELD             State: Establish negative pressurePressure: 363 mbar
31/07/2022 20:47:28    Event: Pressure too low.                     Mode: SHIELD             State: Unprotected       Pressure: 363 mbar
31/07/2022 20:46:50    Event: Pumping finished.                     Mode: SHIELD             State: Establish negative pressurePressure: 422 mbar
31/07/2022 20:46:50    Event: Pressure too low.                     Mode: SHIELD             State: Unprotected       Pressure: 363 mbar
31/07/2022 20:46:28    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 364 mbar
31/07/2022 20:46:17    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 364 mbar
30/07/2022 11:28:48    Event: Pumping finished.                     Mode: SHIELD             State: Establish negative pressurePressure: 421 mbar
cptninc
Friday, August 5th 2022, 2:40pm
Another day, another false leak alarm.
Source code
1
2
3
4
5
6
7
8
9
10
11
12
13
14
15
16
17
18
19
20
21
22
23
24
25
26
27
28
29
30
31
32
33
34
35
36
37
38
39
40
41
42
43
44
45
46
47
48
49
50
51
52
53
54
55
56
57
05/08/2022 05:05:52    Event: Pressure setpoint changed.            Mode: SHIELD             State: Protected         Pressure: 347 mbar
05/08/2022 05:04:36    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 345 mbar
05/08/2022 05:04:34    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 345 mbar
05/08/2022 05:04:24    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 345 mbar
05/08/2022 05:04:02    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 344 mbar
05/08/2022 05:03:52    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 343 mbar
05/08/2022 05:03:10    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 343 mbar
05/08/2022 05:02:59    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 342 mbar
05/08/2022 05:02:57    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 342 mbar
05/08/2022 04:55:41    Event: Pressure setpoint changed.            Mode: SHIELD             State: Protected         Pressure: 347 mbar
05/08/2022 04:55:19    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 346 mbar
05/08/2022 04:55:08    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 346 mbar
05/08/2022 04:55:06    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 346 mbar
05/08/2022 04:54:55    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 345 mbar
05/08/2022 04:54:36    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 344 mbar
05/08/2022 04:54:25    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 344 mbar
05/08/2022 04:54:21    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 344 mbar
05/08/2022 04:54:17    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 344 mbar
05/08/2022 04:54:06    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 343 mbar
05/08/2022 04:53:57    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 343 mbar
05/08/2022 04:53:56    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 343 mbar
05/08/2022 04:53:29    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 342 mbar
05/08/2022 04:53:15    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 341 mbar
05/08/2022 04:53:05    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 341 mbar
05/08/2022 04:52:54    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 341 mbar
05/08/2022 04:52:45    Event: Pumping finished.                     Mode: SHIELD             State: Establish negative pressurePressure: 413 mbar
05/08/2022 04:52:45    Event: Pressure too low.                     Mode: SHIELD             State: Unprotected       Pressure: 340 mbar
05/08/2022 04:52:40    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 340 mbar
05/08/2022 04:52:33    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 340 mbar
05/08/2022 04:52:22    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 341 mbar
05/08/2022 04:52:20    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 341 mbar
05/08/2022 04:11:55    Event: Pressure setpoint changed.            Mode: SHIELD             State: Protected         Pressure: 347 mbar
05/08/2022 04:11:15    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 346 mbar
05/08/2022 04:11:04    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 345 mbar
05/08/2022 04:10:46    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 345 mbar
05/08/2022 04:10:44    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 345 mbar
05/08/2022 04:10:33    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 344 mbar
05/08/2022 04:10:32    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 344 mbar
05/08/2022 04:10:21    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 344 mbar
05/08/2022 04:10:09    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 343 mbar
05/08/2022 04:10:01    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 343 mbar
05/08/2022 04:09:43    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 342 mbar
05/08/2022 04:09:04    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 340 mbar
05/08/2022 04:08:53    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 340 mbar
05/08/2022 04:08:44    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 340 mbar
05/08/2022 04:08:33    Event: Pumping finished.                     Mode: SHIELD             State: Establish negative pressurePressure: 403 mbar
05/08/2022 04:08:33    Event: Pressure too low.                     Mode: SHIELD             State: Unprotected       Pressure: 339 mbar
05/08/2022 04:08:33    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 339 mbar
05/08/2022 04:08:30    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 339 mbar
05/08/2022 04:08:19    Event: Pumping finished.                     Mode: SHIELD             State: Establish negative pressurePressure: 406 mbar
05/08/2022 04:08:19    Event: Alarm: Pump runs too frequently.      Mode: SHIELD             State: Establish negative pressurePressure: 339 mbar
05/08/2022 04:08:19    Event: Warning: Pump runs too frequently.    Mode: SHIELD             State: Establish negative pressurePressure: 339 mbar
05/08/2022 04:08:19    Event: Pressure too low.                     Mode: SHIELD             State: Unprotected       Pressure: 339 mbar
05/08/2022 04:08:08    Event: Pumping finished.                     Mode: SHIELD             State: Establish negative pressurePressure: 401 mbar
05/08/2022 04:08:07    Event: Pressure too low.                     Mode: SHIELD             State: Unprotected       Pressure: 339 mbar
05/08/2022 04:07:51    Event: Pressure setpoint changed.            Mode: SHIELD             State: Unprotected       Pressure: 341 mbar
03/08/2022 18:31:07    Event: Pumping finished.                     Mode: SHIELD             State: Establish negative pressurePressure: 402 mbar
cptninc
Friday, August 5th 2022, 3:05pm
I have now manually changed the vacuum settings from the ones that the setup wizard selected. Perhaps this will help. The new settings are:
  • Maximum Negative Pressure: 475 mbar
  • Set Point Negative Pressure: 435 mbar
  • Minimum Negative Pressure: 400 mbar
  • Use Adaptive Pressure Preset: No
Similar threads